Hello,

I have an Emerson Commander SKC3400400 VFD

It says

Input: 3 phase

Input Range VAC: 342 to 528 Volts AC

My instalation is 3 phase 230V, and the motor i want to control is 3phase 230V

Will this VFD work with 3phase 230V supply or only with 3phase 400v supply ?

Thanks!
 
No it will not. It tells you right here:

Input Range VAC: 342 to 528 Volts AC

230V < 342V.

You MIGHT be able to get a transformer to boost your 230V supply to 400V, then program the drive to put out 230V max to the motor. But this can be hard on the motor because the DC bus voltage that comprises the PWM pulses will be based on the 400V input, which increases the stresses on the 230V winding insulation. It would be better to just buy a 230V drive.
 
No it will not. It tells you right here:



230V < 342V.

You MIGHT be able to get a transformer to boost your 230V supply to 400V, then program the drive to put out 230V max to the motor. But this can be hard on the motor because the DC bus voltage that comprises the PWM pulses will be based on the 400V input, which increases the stresses on the 230V winding insulation. It would be better to just buy a 230V drive.

Ok. Thanks.

But why I connected it to the 230v supply and it turned on. The display at least boot

I havent tried to turn the motor ON
 
The drive internal logic power supply will run off a very low internal bus voltage. So the drive will "power up". But, as jraef says... don't try and run your motor, unless you don't mind buying a new one
 

Similar Topics

I'm using an Automation Direct GS20 VFD for the first time and I have a question for the Automation Direct gurus regarding the recommendation of a...
Replies
2
Views
1,104
Hi, I found strange situation on site, 4kW motor D400/Y660 volt wired in Y (660V) connected to 400V VFD output. Frequency setpoint was 120Hz. What...
Replies
14
Views
3,312
Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
Replies
6
Views
2,628
Hello, all! Doing panel VFD (PF525) wiring. Question about the wires on the VFD T1-T2-T3 output bus. The plan is to connect the T1-T2-T3 outputs...
Replies
16
Views
5,974
Hi Guys Just a quick one. I want to procure a soft starter for a Pump Motor I want to confirm this: IS SOFT STARTER SAME AS A VARIABLE FREQUENCY...
Replies
13
Views
3,298
Back
Top Bottom