Hello Everyone

I have a Delta VFD, after it is supplied by the three phase voltage at the beginning it displays nothing, then after about 5 minutes it starts working and it displays the set frequency.

What might be the problem ?

Thanks in advance for your replys.

IMG_20221108_120053.jpg
 
The three phase power is run through 6 power diodes to charge a DC bus (bank of capacitors)


If a single diode fails that phase will stop charging on that polarity (IE - C is positive)


If multiple diodes fail it will cut out more of the 6 Phase/Polarity possibilities. It seems like enough diodes have failed to take 5 minutes to charge the buss to operating voltage.
Of course it could also be bad capacitors, or even that the buss charges OK but the internal 24VDC (or 12V) power supply to power the logic circuits is going bad.
 

Similar Topics

I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
Replies
1
Views
78
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
184
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
3
Views
173
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
Replies
14
Views
310
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
Replies
13
Views
492
Back
Top Bottom