Vfd ??

porky

Member
Join Date
Oct 2002
Location
Maia
Posts
76
From the attachment what would you guys /gals out there consider the nominal RPM & Frequency to be... to program in the VFD.??

I´m puzzled, lol it does not take much though :sick:
 
Last edited:
The pump is driven by a 2-pole 45kW motor (notice the 2FX200XG-02/F). It should be fed with a 3-phase 400V supply at 62Hz instead of the standard 50Hz.

A very unusual type of motor!

Make sure you set the base frequency to 62Hz and limit the max frequency to 110Hz, both setpoints should be available on any standard VFD. This way, the VFD will only deliver 400V at 62Hz and up, so you have constant power in the permissable range.

If you're planning on using this pump in the US, you also have to take the different line voltage (440V, or is it 460V?) into account. In this case you also have to limit the base voltage to 400V.
 
This nameplate plainly says that the field weakening point is 101.5hz. Field weakening occurs when the voltage no longer rises at the same rate as frequency.

Clearly then, since the rated voltage is 400v, the voltage should continue rising linearly up to 101.5hz and then hold constant (field weakening) from 101.5hz to 110hz.

The analysis I did and the set points I gave you, porky, over on the motor BBS are the right ones to use.
 

Similar Topics

Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
2
Views
82
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
3
Views
124
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
Replies
14
Views
264
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
Replies
12
Views
345
Hi, I would like to assemble a simulator/practice booster pump system that uses PID to maintain steady water pressure under various outlet demands...
Replies
0
Views
95
Back
Top Bottom