Watlow EZ-Zone controllers

Steve Bailey

Lifetime Supporting Member + Moderator
Join Date
Apr 2002
Location
The boondocks of Western Massachusetts USA
Posts
8,591
I am tasked with connecting multiple Watlow EZ-Zone PM controllers to a Watlow EZ-Zone RUI/Gateway unit. They show up to 16 controllers connected to a single gateway over an RS485 two-wire cable. I'm accustomed to putting terminating resistors at the physical ends of RS485 cables, but the Watlow manual doesn't show them on the Watlow standard bus side, only on the Modbus RTU side when you choose that option.
Does anyone have any experience with a setup like this? Can I leave the cable unterminated and reliably get the data from the controllers to the gateway?
 
Page 6 of the gateway manual:

• A termination resistor may be required. Place a 120 Ω resistor across T+/R+ and T-/R- of last controller on network.
 
I already have that manual. I know how to read it.
My question was about whether anyone has any personal experience with running the Watlow standard bus unterminated since Watlow doesn't show a terminating resistor in their manual. I found that fact to be unusual.
 
No, no experience with this device.

But Watlow's wording suggests that Watlow has placed a terminating resistor across its terminals. I suspect that if you measure the resistance across (+) and (-) 485 terminals when the power is off, you'll find a resistance > 100 ohms.

They're probably assuming that their gateway will be at one end of the multidrop daisy chain with only the last controller needing a terminating resistor.
 

Similar Topics

I have a job with two EZ-Zone Ethernet/IP Controllers connected to a CompactLogix L18ERM. I've followed the documentation I could find in setting...
Replies
3
Views
3,745
Hello everybody, I want collect data from EZ-ZONE PM (PM6C2CH-AAAAAAA). I saw in datasheet it only support standard IEA-485. And datasheet donot...
Replies
2
Views
2,509
I'm a newbie who started a job as a repair tech recently. I've had plenty of luck with ABBs, Allen Bradleys, and a few others, but I can't seem to...
Replies
1
Views
165
Good Eve Gentlemen, We had this cold room which was converted to hot room before I joined this work. Everthing was fine until a month ago, they...
Replies
9
Views
2,101
My system has an Allen Bradley PLC, Red Lion CR3000 HMI, and a Watlow F4T controller. I am able to read registers from the Watlow F4T via Modbus...
Replies
0
Views
1,643
Back
Top Bottom