which product should i use for SCADA on DH-485 network?

mrzhao

Member
Join Date
Jun 2006
Location
Shenzhen
Posts
26
I have a project now.
There are 7 AB SLC 503s in the plants, i would add 2 SCADA computers to monitor the SLC 503s. I am planning to use DH-485 networking for them.

which product should i use for the computers?

1784-PKTX is too expensive, could i use 1761-net-aic or 1747-PIC,1747-UIC ?

thanks for any advice!
 
DH485 comms will slow exponentially as you add nodes. If your two SCADA systems are carefully configured you may not see too many delays. It might be best if you used two different networks to keep the node count low on each. That would mean a NET-AIC at each 5/03 and a DH485 bridge (or two) ar each PC.

Look here:
http://www.ind-concepts.com/Allen_Bradley_PLC_Cables.htm

About halfway down the page there is a PIC replacement for an economical DH485 bridge (real serial port required).
 

Similar Topics

Good Afternoon , It has been decades since I have done anything with Siemens . What is the Siemens name of their Servo Product Line and what...
Replies
10
Views
216
Hello All, I'm looking for some opinions and Ideas for guarding the product entrance of a palletizing robot cell. Please see the attached...
Replies
7
Views
534
Respected Members; I am going to design the PLC control system. The requirement as under: 1. Input/ Out put modules are SIL 2 certified. 24...
Replies
2
Views
429
I've got an issue opening a project in TIA Portal v16. When the file is opening, I get the message that says "Optional products used in the...
Replies
2
Views
788
I am new to Siemens, and just looking into their HMI software. Does Siemens have a product similar to FactoryTalk View SE? I am looking to have...
Replies
14
Views
1,803
Back
Top Bottom