Wiring 0-10VDC Analog input
sparkytex
Jun 2013
Port Hardy B.C.
354
Hey guys,
I've only dealt with wiring 4-20mA analog inputs as the majority of instruments I've used are 4-20mA. I'm using a Mitsubishi VFD and their analog output I'm using to send the VFD's 0-60Hz signal to the PLC is 0-10VDC on terminals AM and #5.
PLC being used is a 1769 AB compact logix. The card used is a 1769 IF4I 4 channel analog input module. If I'm using CH.Data.0 on the card would I just wire it as Analog common (-) from VFD to CH0- and the Analog positive (+) from VFD to CH0+.
I'm fairly confident in scaling the 0 to +10VDC on the PLC but just unsure of the field wiring on the card and if I need any jumpers etc.
any help is greatly appreciated.
- Tex
According to the manual for that card, you are correct. Common to ch0- and Positive to ch0+.
Bubba.
Posted this to Reddit with little success, so I figured I would share it here as well. Very new to PLCs, but figured I would give it a shot to...
123
Hello Folks, Has anyone configured a Momentum high speed counter on Unity 13.1. We need the wiring diagram for Momentum High speed counter and...
78
Hey guys, the scenario is: I have already completed the drawing package for my system utilizing an A-B 440R-N23126 (Minotaur) safety relay. SoS...
141
Maybe a stretch to call this a PLC question, but it does connect to a PLC input. I have two German switches: Sick WL9LG-3P2232 And a...
113
Hello I wanted to ask some questions about the G120C drive and the protection for it. I want to control a pump, with the motor rating of 5.5 kW...
199