will see if I can make it work.
As Bernie mentioned you need to get the "time" into the proper format. Here is one way that may save you some frustration. I hope that my use of V2000 and the manual's use of V2000 do not cause confusion. In my example the double words V3000 and V3001 are loaded into the time clock
PLC 06
// Rung 1
// Address 0
#BEGIN COMMENT
"When the ""set time"" button on the HMI is pressed the values from the HMI are formatted "
"for insertion into the PLC time clock"
"To get the minutes from a value of say 45 to 4500 we multiply by 100, then we add the "
"seconds"
"Finally we use the ""TIME"" instruction to load the values in V3000 and V3001 into the PLC "
"timeclock"
#END
STRPD C0
LD V2001
MUL K100
ADD V2000
OUT V3000
LD V2002
OUT V3001
TIME V3000
// Rung 2
// Address 9
END
// Rung 3
// Address 10
NOP
#BEGIN ELEMENT_DOC
"C0","","","""set time""momentary pushbutton from HMI"
"V2000","","","seconds from the HMI"
"V2001","","","minutes from the HMI"
"V2002","","","hours from the HMI"
"V3000","","","minutes and seconds formatted to enter into PLC time clock"
"V3001","","","hours ready to enter into PLC timeclock as part of a double word"
#END