Say I produce in PLC-A data A and consume data A in PLC-B and PLC-C. PLC-B and PLC-C can write to the consumed tag, but if they do, does PLC-A see it?
Overall my question is, are produced/consumed tags one directional?
Thank you,
Josh
No. The produced tag will overwrite it. Producer/Consumer is unidirectional. Producer --> Consumer. If you want data to go back to the "Producer" PLC, you will need to setup another Produce/Consumer connection, this time with the "Producer" PLC being the consumer.
JoshM,
Hold on a second! If i understand your question correctly, PLC A writes data to PLC B & C. You also want PLC B&C to write data to the same addresses. if this is true, then you should be aware thet PLC A can write the data to PLC B & C at any time, even in the beginning, 1/3 way, middle, 3/4 into the program or at the end of the scan. the data from PLC B&C could be over written and be lost.
I strongly advise against having PLC B & C write data into registers that PLC A uses. You cannot predict what data you are using.
Not trying to slam you, i had this happen several years ago and they didn't realize for several weeks what was happening.
regards,
james
Why don´t you create another tag and move data from consumed tag whenever you desired or get data from another source. Normally produced-consumed scheme is left the way it is i.e. updated from produced to consumed tag.
You guys are correct. I do not plan on doing this, but was curious how scan time and produced/consumed timing play out. So produced/consumed tags are independent of the PLC scan time throughout the code?
Hi, I'm having an issue in crimson 3.0 when I create a programme using a case statement referencing a fault word that each bit needs to change the...
298
Hello all, I'm currently working on a servo motor linear positioning system (ball screw). I'm all set up regarding communication between my HMI...
111
Hello All: I have a Windows 10 PC running a FTView ME Station 10.00. I have a .mer file version 6.00. It has been running well on it for a long...
180
My R55 Ingersollrand is tripping on motor overload and im falling to see the trip history it is writing Acquarring texts
140
Hi. Not the fist time I'm saying this but just to give a background. 95% of my PLC programming has used Schneider over the last 10 years on...
66
5,058