Yaskawa A1000
So.... where does that leave me? Can I safely connect the A1000 drive to corner-grounded 240V power without letting the smoke out or not? Do I have to remove the MOV filter network in the front end / is that possible?
-rpoet
It's your call, but the only SAFE option in my mind is to install a "drive isolation transformer" ahead of the drive. It would be 230 Delta primary, 230/133V Wye secondary. You don't USE the 133V L-N voltage of course, but it creates what the VFD components are looking for, a solid reference to ground on the input line voltages.
Example only, not an endorsement:
If you were (hopefully) going to use a Line Reactor, you can eliminate that as this transformer will provide the same level of drive protection as the reactor would have.
The compressor is a pre-packaged unit, and comes with a line reactor installed.
I got written confirmation from Yaskawa that the drive would be OK on corner-grounded delta power, for whatever that's worth. They also said I should install "ground fault protection" on the circuit supplying the drive, and when I pressed the tech he couldn't really explain why or how that would help; it seemed like a CYA to me, and goes to your point regarding Yaskawa not really understanding delta power.
Anyway, the drive powered up without any issues, and is running without a transformer. Time will tell if issues crop up.
Ugh. I hate corner-grounded delta power.
-rpoet
Hi, I want to do an electronic line Shaft with Yaskawa A1000. I think a must update firmware. Do is a user that have a firmware for this? I...
780
Hello friends, I have Yaskawa A1000 drive and I want to activate a safety function during starting a drive .🤾 I have assign frequency...
1,751
Im assisting a customer with a Yaskawa A1000 drive. The machine came from China The part number is CIMR-AB4A0023FBA Can someone help me find the...
2,527
I’m working on an application where I would like to mount the encoder on the end of the gearbox instead of the motor Can I hear from any of the...
1,891
Has anyone ever tried to connect an HMI to a Yaskawa A1000 VFD? If so, what HMI did you use and what communications protocol? I want to try to...
2,084