hi all,
i need to know that "are this transmitter convert the measured diff. pressure value to level value or how i can convert it as plc have only the scaling equation."
 
If you want to use differential pressure measurement for Level measurement you must scale the range of it in relationship to the head pressure expected to be in the tank at full. Typical use is "h20, lets say your tank is 10 feet tall, and has water in it, then your scale would be 0-120" h20, or less if you want some wiggle room. Now if it is not water, you must figure out the RD of the product (water is 1.0 RD) so for example. Oil can be.6-.8 RD. .8 x 120 is 96" this is because the fluid is lighter and therefor takes more to make the same head pressure.

it is not a setup in the transmitter, unless you set the display up to % it can resemble level, but the range will still be in "h20. you can also convert that pressure into any of the others after the calculation.
 
Yes so scale the raw value to be 0-100% level as well. not sure what brand plc you have but it should say how to in the manual. also your low pressure side needs o be attached to.top of tank if it isn't open to atmosphere. and then that also can lead to situations where you.need the low side filled with fluid but that's for a later discussion
 
A DP transmitter measures head pressure in units of water column, like mm H2O or m H2O, or inches water column.

Head pressure divided by specific gravity = level

If specific gravity (SG) is 0.90,
then DP of 2.43 m H2O is a level of
2.43m/0.90 = 2.70m liquid
 

Similar Topics

First off, Happy New Years. For those of you working like me, enjoy the doubletime, or whatever compensation you're getting. For those of you...
Replies
10
Views
5,417
how to use test terminal and how to connect them and when we use it?
Replies
2
Views
3,074
I have 3051 cd rosemount transmitter used to calculate dp as it located at danile orfice and LRV=0 & URV=250 , LSL=-250&USL=250 all units is...
Replies
2
Views
3,112
Hi, a customer has an installation on which a Yamatake DCS monitors about 60 Rosemount FF temperature transmitters. The DCS is a Mobdus RTU master...
Replies
4
Views
568
The original Rosemount pressure transmitter was configured to give them the 5 million gallon tanks level in inches. It died so they put in a...
Replies
12
Views
3,570
Back
Top Bottom