rosemount transmitter 3051 cd
When you are out in the field and only have a meter with milliamps (no HART) you can measure the transmitter milliamp signal at the test terminals without breaking the loop. Some transmitters have a Test jumper to short out the diode you are measuring across. Put the jumper in the Test position to use this feature.
There's a diode across the test terminals (behind the scenes). The impedance of a milliammeter is usually less than the diode, so the loop current flows through the milliammeter rather than the diode.
As John pointed out, the test terminals allow you to read the loop current without opening/breaking the loop to insert the millammeter is series.
I did find last week that some ultra-cheapie meters read low by about 20% on the test terminals. They read OK, within 0.02mA when in series, but when put across the test terminals showed significant error.
So, you might want to test your meter on the bench with a similar model that you can force to several output levels to confirm that the meter is reading within a reasonable tolerance for whatever task you're involved with.
By the way, the diagram shows both the HART communicator and the load on the loop terminals, not the test terminals.
I have 3051 cd rosemount transmitter used to calculate dp as it located at danile orfice and LRV=0 & URV=250 , LSL=-250&USL=250 all units is...
3,114
The original Rosemount pressure transmitter was configured to give them the 5 million gallon tanks level in inches. It died so they put in a...
3,576
Hello everyone, I am working with a 8705 flow element mounted to a 8712 remote mount transmitter. From my previous experience with Rosemount...
3,237
Dear all, I have line pressure transmitter with model no.:3051TG4A2B21KE8D4M5Q4Q8S5B4P1T1 when i connect hart communicator 375 to it for...
2,756
i have rosemount transmitter 3051 cd with remote cell to measure level after intalling it there is no reading i check everything related to plc...
7,707