1761-Net-Eni D module

macstorm

Member
Join Date
Jan 2014
Location
india
Posts
17
Hi,
I couldnt assign IP address to 1761-Net-ENi D series module. I do know there are lot of discussion went in this forum since 2003. I have did alll troubleshooting methods but there is no luck.

I have supplied 24VDC to the module.

1. I have connected Rs232 to PC and opened the ENI utility, and assigned the IP address when click download to ENI Rom "it says unable to connect check the cable/switch.

Second method.
2. I have connected Ethernet to 1761 module then used the Comdir, when i clicked load from ENI it says unable to connect.

After the power up cycle the RX/TX is blinking with amber(red).
Finally I couldnt assign the IP address. Pls suggest me some solution
 
Yes iam using 1761-CBL-PM02 cable.
Verified the com port in device manager it indicates Com port 1.

So i selected the Com1" and baud rate is 9600

I have checked with all baud rates but no luck
 
I think its module fault.

I have checked the power up sequence for the 1761-net-eni D series, it is said that Fault Led should flashes for 2 -4 sec. But in my case, the fault Led didnt flashes even once.

So my guess is that my module is fault
 
Sounds like a bad module. At times rslinx will retain control of the serial port. Try to reboot without starting rslinx again. This works sometimes.
 

Similar Topics

"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
162
Good afternoon guys, does anyone recommend a direct replacement part for Allen Bradley's 1761-NET-ENI devices? We have a lot of these in our plant...
Replies
9
Views
1,020
Hello, currently I have a micrologix 1200 (1762-L40AWAR )connected to an HMI panelview 600(2711-T6C3L1X) via the 1761-net-aic module, I want to...
Replies
13
Views
1,807
I have decided that instead of upgrading the drives & plc at the same time on my project i would just do the drives for now as just getting them...
Replies
23
Views
9,047
Our company has many of Rockwell's beloved NET-ENI modules to get SLC 5/03's onto our network. They have the issue of faulting out if more than 3...
Replies
2
Views
1,929
Back
Top Bottom