plcstu1980
Member
Hi, how do you go into config mode to change the ip address of a 2014 PV+ 1000 HMI. If you don't know the ip address and login password?
Thanks, Stuart
Thanks, Stuart
plcstu1980 said:...PV+ 700/1000 config mode...
Hi, how do you go into config mode to change the ip address of a 2014 PV+ 1000 HMI. If you don't know the ip address and login password?
Thanks, Stuart
jstolaruk said:When the HMI boots, look for a small white square to appear in the bottom left of the screen and press it before it disappears, it should boot up into the config menu without starting the application.
jstolaruk said:When the HMI boots, look for a small white square to appear in the bottom left of the screen and press F1 before it disappears, it should boot up into the config menu without starting the application.
What jstolaruk has posted is correct if it is a Touch or Key/Touch display module.
However, if it happens to be a Key only display module then...
(Apologies for the edit j!)
It may very well be a Touch module, but without the Catalog Number we can only assume, and we don't like to assume, especially when it's not necessary to...:site:
Regards,
George
plcstu1980 said:...It's CAT is 2711P-RP9D, touch screen. No white box on the newer HMI's, any other way to config?...
plcstu1980 said:...how do you go into config mode to change the ip address of a 2014 PV+ 1000 HMI...
Brilliant, very informative i can now get into the ConfigOK, we're getting somewhere, but just so you know, that is still not a full Catalog Number. So I still have to deduce some facts here...
2711P-RP9D is the Catalog Number for the Logic Module which is just one part of a base-configured PanelView Plus terminal; also known as an Assembled Terminal.
An assembled PanelView Plus terminal will be made up of at minimum a Logic Module and a Display Module, and optionally a Communications Module.
Let's say you have your 2711P-RP9D Logic Module and a possible 2711P-RDT10C Display Module. Combined they would make up the assembled Catalog Number of...
2711P-T10C4D9
This is a full Catalog Number for a factory assembled PanelView Plus 6 1000 terminal...
T = Input Type - Touch
10 = Display Size - 10.4"
C = Display Type - Colour
4 = Communications Option - Ethernet, RS-232, USB
D = Power - DC
9 = OS - Windows CE 6.0 with extended features
The first three items in the Catalog Number are determined by the Display Module 2711P-RDT10C, and the last three are determined by the Logic Module 2711P-RP9D.
If you have an assembled terminal then you should see a full Catalog Number on the Logic Module's sticker in the top right above the barcode.
Here is an example (marked in Red), image courtesy of PLC Hardware...
As you can see from the photo you have quoted just the Logic Module Catalog Number which is on the bottom right of the sticker (marked in Green).
If you look at the back of the Display Module itself, you should see another sticker with its Catalog Number.
Here is an example (marked in Blue), image courtesy of PLC Hardware...
If you purchase just a Logic Module then the sticker will have no Assembled Catalog Number in the top right corner.
Here is an example (marked in Orange), image courtesy of PLC Hardware...
I know that this should be a PanelView Plus 6 terminal as the older PanelView Plus terminals all use 2711P-RWx Logic Modules and the newer PanelView Plus 7 terminals do not use removeable Logic Modules. Your Logic Module is specific to the PanelView Plus 6 family.
Also, the older PanelView Plus terminals went to pasture in 2012. So a 2014 terminal is too new to have been of the older stock which displayed the White box. Something I missed from your opening post.
So, now that you "appear" (I still would prefer the Catalog Number...) to have a newer PanelView Plus 6 terminal, we can say that the older White box method is not relevant here for getting into Configuration Mode.
For the PanelView Plus 6 terminals...
By pressing the recessed Default button on the back of the Logic Module you can restart the terminal in Maintenance Mode. You can see this button in the last image above.
Note: This is not Configuration Mode.
You must use a USB keyboard to navigate the Maintenance Mode menu and scroll down and select Special BOOT Action>SAFE Mode.
You then go back to Continue booting with selected options and the terminal will BOOT into Configuration Mode. On the first screen you will see the terminal's current IP address and Subnet Mask. You can then navigate through the Terminal Settings menu to change the terminal's IP address, which is what you originally said you wanted to do...
See the following technote...
119811 - PanelView Plus 6: How do you access the Maintenance Mode/Configuration Screen
Access Level: Everyone
Regards,
George