I'm firing and output and I need it to stay on for at least 2 seconds...

What's the best way to do this?

Studio 5000
L27-ERM CompactLogix
Discrete 24V Output


Thanks,

John Whited
 
Create a seal in circuit that has a timer branched with the output. When the timer is done, break the seal.

Maybe not the best way, but a way...
 
Here you go:

[XIC(switch),XIC(output)]XIO(delay.DN)[OTE(output),TON(delay,?,?)];

Ignore the aliases in the image below, but had to test it for you :p

(Click to enlarge)

 
Good thinking dragonx however the OP needs to know there is a slight difference in the two methods...

if the input is switched again during the two seconds, using the TON method the output delay will not be extended. Using the TOF method it will. Which one suits best for the OP, he will need to decide.
 

Similar Topics

Hi all, Well, here I find myself at a former client after I left water treatment trying to help him get the plant back up and running after a...
Replies
2
Views
1,086
Hi all! I have one question, it might be simple for one of you but I spent hours searching and reading through different platform until I found...
Replies
11
Views
1,658
I had a customer ask me to investigate what state a digital output would be in a PLC5 if the the processor faulted or was put in program mode...
Replies
1
Views
1,189
I just had a weird one last night and was wondering if anyone else has ever seen this. A SLC5/05, 7 slot rack. One thermocouple input, One 18...
Replies
3
Views
2,128
Hello, I have a question regarding the analog output modules on a AB Micro850. I'm not getting an output to my valve and when I put a meter on it...
Replies
2
Views
1,549
Back
Top Bottom