In our PLC5 processor we have the last analog value being overwritten on a couple of cards.
The values from the next card down are being sequentially written over the last analog value of the previous card. (see pic)
I looked in Block transfer programming but can't see any errors.

PLC5 WTF1.jpg
 

Attachments

  • L140_FRY.zip
    300.3 KB · Views: 4
Since this is a PLC-5 system and has been presumably running properly for years, what has recently been changed?
 
Yes, it has been running for years, and for example N11:11 (SAPP Tank temperature in pic) In the N11 data table stays constant at 1300.
But when you look at the data column in the IFE information page the N11:11 value flips to 287 (from N11:16)
then 1573 (from N11:17)
then 1573 (from N11:18)
then 586 (from N11:19)

The value is changing in the data column (white column) but not the data table value....
Could this be caused by a BTW or BTW setup wrong?
 
what I would do is to search for the first register that is changing which isn't supposed to - do a global search all.

that will tell you every rung where this value is being written into.
remember, the last rung that references the register is the owner !

repeat for the other registers.
james
 
The only place N11:11 (for example) is being written to is in the BTW of the Analog input card.
But it's not the value of N11:11 that is changing, it's just in the white data box of the Analog module information page.
The values from the other analog card keep cycling in through the data box.
 

Similar Topics

Hi: I recently tried connecting 2 new single-ended 4-20mA analog inputs to an existing 1771-IFE. The IFE is in a RIO chassis. The values coming...
Replies
4
Views
1,405
I've got a 4-20ma pressure transducer connected to an analog card on an AB PLC5. Under the setup for the card, I have to set a raw minimum and...
Replies
12
Views
7,379
My goal is to get an analog signal from a SLC-500 remote rack back to a PLC-5 main rack. Is this possible? If so, I may need some help. I've set...
Replies
4
Views
1,769
I know there have been a couple different posts on this subject but I was still unable to get the final information needed. In my facility we...
Replies
44
Views
8,740
Hey guys, I have a problem that is puzzling me on a PLC 5 system. I am using a 4-20mA analog output (1771-OFE2/B) straight to a Powerflex 4m...
Replies
7
Views
3,690
Back
Top Bottom