..... it probably takes a couple minutes until you can see the effect of the change.....
....the gas sensors can only take a reading every so often (5-10 minutes)....
what's the limitation - the delay before the gas mixture can be measured, or the measurement rate of the sensors ?
is this a potential "roll-up" in time, meaning that the control algorithm sees a random time delay of the asynchronous effect and measurement ?
can the gas sensors measure faster, or is it a sample time they need to analyse the gas ?
can the analysers be "reset" to synchronise with a CV output change ? this could minimise or stabilise the CV -> PV delay, which might make it easier to control.
In trying to appreciate a complex loop control, I often think about what a person would do faced with the same decisions....
Things I consider -
1. If the PV won't change for 5 minutes after I adjust a valve, why would I look at it every 100mS....
2. Can I use historical data to make an adjustment....
3. What stops me from "over-cooking" my response, sort of leads back to 2. A person would have gained "experience".
There are always challenges on some closed-loop controls, and sometimes PID control just can't be made to work efficiently.
I'm interested to see Tom expand on his "floating control"