This may be an easy question for some...but I'll need a little guidance.
I have a project where under a particular condition I will need to force a PCV normally controlled by a PID loop to 15% open.
Under any other circumstances, the loop will control the valve.
Is there a good, clean way to do this? I guess I could think of a couple ideas, but they are not real clean in my opinion.
Thanks,
Burch
Ladder or FB version of PID?
PID: Place PID in software manual and set the output to 15%.
PIDE: Set CV Init value to 15% and set and hold the CV init request bit.
Are you holding it at 15% for some period of time or are you trying to initialize it to 15%?
Second guessing myself here, need someone to either tell me I'm wrong or confirm that my thinking is correct please. I have an equal-percentage...