Allen Bradley 525 inverter

eebads2391

Member
Join Date
May 2008
Location
Stockport
Posts
112
Hi guys ,

I'm running a small screw transfer conveyor from an Allen Bradley 525 inverter

It is fully covered and trqnsfers product from the bottom of a silo bin out into a hopper

I want it to run on power up and have it linked between t1 (24v ) and t2 ( dig in run fwd )

I also have parameter a543 set to 1 to allow run on power up

My question is this ,

I now want to drive the inverter with a 0-10v signal but need a way of making sure the
The minimum start speed is 7hz so I don't stall the motor by trying to run it too slow
Is this possible to define in the inverter

Thanks in advance
 
Parameter 43 "Minimum Freq" is what sets the minimum speed command from the VFD.

Are you saying that you need to start at a higher speed and it is okay after that to drop below 7hz depending on your analog input?
 

Similar Topics

Got this new to me powered on today and have no main air and the only problem I have found is the f059 on the vfd. S1 has 24v, none on S2, and 48v...
Replies
10
Views
474
hi, I have a PLC that has been running for a few years now, and recently the SMTP was moved to a different server and IP address. we noticed...
Replies
10
Views
3,063
Just had an interesting dilemma. 6 powerflex 525’s changed their max hertz on 5 different machines all are connected via Ethernet but do not work...
Replies
9
Views
2,532
we have a 525 drive with a 25-comm-f2p module. that was giving us 4 solid red light for communication. replaced module now we get port light is...
Replies
1
Views
1,345
I have a question about a couple of parameters on the 525 Drive. The parameters are as follows: P033 Motor OL Current P034 Motor NP FLA What...
Replies
5
Views
4,459
Back
Top Bottom