Hi,

I'm sourcing for a RS232 to RS485 convertor (Class 1 Div. 2), oil and gas application.

We are connecting our Allen Bradley PLC, MLX 1500 (RS232) to DCS (RS485) in Modbus protocol.

Hope someone has experience in such convertors can guide.

Thx.
 
My two favorite RS-485 converter vendors are

www.bb-elec.com

www.robustdc.com

Since the protocol is Modbus RTU, the connection will be half-duplex. You do need to find out if your DCS uses 4-wire or 2-wire RS-485.

You will probably have to inquire with the vendors about their Class 1, Div 2 ratings.

The Allen-Bradley 1761-NET-AIC converter is Class 1, Div 2 for Groups A,B,C,D and uses 2-wire RS-485 signalling with an isolated common wire. Since you are already using Allen-Bradley hardware, this interface device may be ideal if the DCS also uses 2-wire RS-485.
 
Ken: Thx for ur info, I've chk out the bb & robus comm, but it's isolated devices, not Class 1 Div 2, right? Thx.
 
Last edited:
Mickey: I've chked out the Sixnet, but can't find any RS232-RS485 convertor, can you please let me know the catalogs number. Thx :)
 
The hazardous environment ratings are not prominent in B&B or Robust DC's product data sheets, but that doesn't mean they don't qualify. A-B is accustomed to putting all the agency certifications on the product data sheet because they are accustomed to having to pass a handful of different agency tests wordwide.

Of primary importance is the implementation of Modbus RTU on RS-485 at the DCS end. If you don't know EXACTLY how it's done, you can't make the right selection.
 
Ken Roach, you are correct, after explaining to our customers, they agree to settle with ADAM, isolated convertor, just cost less than 90USD.

Thx for your inputs.
 
They don't have converters but they do have modems rated for hazardous areas. Use your own two wires for phone lines.
 

Similar Topics

i have an device which can support serial (RS485,RS232),CAN protocol . i want to connect it to an existing MIB 1553B bus ,what device will I need...
Replies
0
Views
97
Hello: I have to connect a RS232 Modbus RTU slave that only has Tx, Rx and GND signals to a Modbus RTU master. However, all RS232 to RS485...
Replies
3
Views
234
HI All, does anyone know if you have to change a cp 341 rs232 and use a cp341 rs485, what changes have to be made to get it to...
Replies
0
Views
1,343
Hi guys Just wondering if anyone has succesfully read barcode data from these barcode scanners to a plc via rs232 or rs485? If so do you guys have...
Replies
0
Views
1,463
I'm working on an application to have a ControlLogix 5561 communicate with a Telesis TMC420 pin stamp / dot peen controller. The Telesis unit has...
Replies
18
Views
9,971
Back
Top Bottom