Anyone know where I can get maps jr software?
I have an older omron CQM1-CPU43 that was
Programmed using maps jr! Help!!!
 
I stated "maps software" i found info relating to "CAPS" software
And keys. I have an omron plc that was originally done
In caps jr. Its down, need any help. Is the key hardware
Only?? Any way around getting online with cx programmer??
Or anything else??
 
No longer available - Wamco have been out of business for years. Unless you get lucky and someone has a copy.
 
Just to add to BobB's response.

CAPS required a hardware dongle on the parallel port.
Software will not work without the dongle.

You can certainly connect to the plc with CX-Programmer.
You would not have the descriptors / symbols, but would have full access to the code.
One of the dip switches will reset the port to default if you are having connection issues. See attachment.

Wish I had better news for you.

CQM1_DipSwitch.jpg
 
Last edited:
Thank you for any help.
I am Supposed to be getting dongle via ups from OEM to get this back online
I have CX programmer V2.1 OLD.. But I could not get online or even see the node of his PLC. I even swapped out comm card in CPU as customer had already blown RS232 port. I had to previously replace the 232 IC on the comm card to get it going a couple months ago.
The OEM said I could not see program etc. due to Caps and dongle??

I am not familiar with this software "yet"
 
That's where I purchased my cable from (CQM1-CF102)
I was on the peripheral port, but no connection.
I have another cpu to verify I could see comms. cable and cx is working, but I did not have dip switch 5 set to on, just 3&4
they have a operator panel on the rs232 d sub port already..
do you think that switch 5 may be the reason I cant see PLC node?

Thanks for your help..
 
I would try setting Switch 5 to ON.
You will need to cycle power after changing the switch.

This should reset the comm parameters to default: 9600,7,E,2.

If you cannot connect, try 2400,7,E,2.

Not sure how old your CPU is. Original CPU default was 2400.
Later models improved to 9600.

If you get connected, record the values in DM6645, 6646, 6650, 6651. This will let you figure out the settings for each port.

Hope this will help.
 

Similar Topics

i need, Omron NT31 Programming Cable Pinout PC to NT31 for CX DESIGNER Can any one share?
Replies
9
Views
3,117
I got a request from our IT dept asking about our factory floor SCADA system IP addresses. He wants to know if certain processes are fully...
Replies
0
Views
1,430
I'd like to pull in an Autocad P&ID to one of my C-more screens. It appears a bitmap is all that is allowed. First time working with one of...
Replies
4
Views
2,202
I would like to take a bitmap (symbol) and edit it. Is there a way to export them. Or can Redlion give me a copy...... I want to change the...
Replies
5
Views
2,393
The Micrologix Programmable Controllers - Instruction Set Reference Manual describes analog input data files for two different modules and analog...
Replies
16
Views
15,971
Back
Top Bottom