Powerflex alarm.jpgHi,

Currently our machines uses CL5K v.15 with 3 motors and the speed, on & off are being controlled by Yaskawa drive through ETHERNET. The problem is 1 drive (60HP) broke down. I have replace the drive with POWERFLEX 753 with IPCard 20-750-ENETR. I followed the instruction but I having faulted ETHERNET MODULE.

The drive IP address was set using NODE ADDRESS SWITHES, I assumed it was set up properly since it was recognized by RSlinx.

I attached the screenshots of the configuration, please help figure out the mistake (I not enough knowledge on this just following the manuals).

CL5K.jpg
 
Why are you using a generic module for a powerflex? You should install the PF75x AOP and use the powerflex in the io tree. Those generic modules are probably for your Yaskawa drives. You don't set up a PF the same...it will be much different as will the code to control it.
 
Last edited:
Rortmee..
Am using v15 of CL5k according to the manual the generic module is the option.. now i already estblished the communication but the speed reference did not transmit to the powerflex..
Powerflex reference source set up is... Para 545--- P00 powerflex--- Port 4 (where the ip card is connected)...
 

Similar Topics

Dear forum members, By reffering to the blue labelled command on the attached file, Could you tell me what PLC register that is being limited by...
Replies
0
Views
66
What is the best way to extract the hour and minute from the register that comes from Yaskawa VFD. In studio 5000 I have a register saved as INT...
Replies
3
Views
160
Hi sir I has a equipment use Yaskawa GL60s PLC via P150 developer,we want to upgreat the system to New,but we have some problems For example: On...
Replies
0
Views
159
Hi Everybody, this may be one for you motion control guys. We have been tasked with interfacing some Yaskawa drives into a project where the...
Replies
0
Views
286
Hello, We have several Yaskawa GA800's installed in our plant. They are all controlled via Ethernet and they work fine. However, they all get...
Replies
0
Views
504
Back
Top Bottom