Quick question that I have been banging head on wall from.

For some odd reason, I cannot toggle bits in the RUN or REMOTE RUN mode, and only can toggle outputs while in programming mode. None of the forces seem to have any effect at all on either mode. As I check the config tables I cannot change states at all. This is starting to get very frustrating.
Im wondering if it may be in the settings or something to do with scan time.
Please help
Cheers
 
It could be that the bits you are trying to toggle are being changed back elsewhere in the program. If I need to go around a certain bit to get an output to turn on I'll usually use a branch with a test bit that I can toggle as needed. Just be sure to remove the branch and test bits when you are done.

*And BCS wins this round of the typing race!

Bubba.
 
Kevin,

You disappeared so I guess you got it.

If not one last thing that might be happening.

If you are going from RUN to PROGRAM and then back to REM RUN......the plc is not running.

Switch the PLC to RUN, then to REM RUN and give it a try.

The logix icon will be spinning when you are online with a functioning PLC.

BCS
 
Last edited:
Still Have not figured it out. I am in Remote Run as you had stated. I think that you are right in the sense that there is something wrong with the program. I am not trying a very difficult program. it is simply a seal in rung. Just cannot seem to figure out why I am unable to toggle bits. The logo is spinning and I know my PLC is receiving the signal from the indicator light. Any more suggestions as to what the cause is?
Thanks
 
It may also help if you tell the forum the bit address you are trying toggle. Along with the program.
 
I'm betting on guydegraeff's line of reasoning ...

Initially you refer to both toggling bits and forcing them. which is it?

he's absolutely correct: a TOGGLE and a FORCE are NOT the same thing - although many people believe that they are ...

and the following statement is troubling:

I know my PLC is receiving the signal from the indicator light

an indicator light is an OUTput ... PLCs do not RECEIVE signals FROM lights - instead they send signals TO lights ... or did you mean to say something like the following instead? ...

I know that my PLC is receiving the signal that I am sending it - because the indicator light changes state ...

I'm not trying to be picky - but remember that we can't see what you see ... we only know what you TELL us - so details make a big difference in how much detailed help we can give you ...

also ... do you have actual real-world outputs (lights, etc.) hooked up to your system - or are you just looking at the "green on the screen" indications on your computer? ... in that case, you need to know that in Allen-Bradley systems, FORCES do not affect the ONE/ZERO status of OUTput bit/boxes - so the "green on the screen" indications will not change state (if that's what you're trying to do) ...

TIP: show us a screen shot of what you're seeing - and give us some more detail ... I'm sure that we can help - but right now we're just guessing at what you're dealing with ...

and welcome to the forum ...
 
Last edited:
And another WAG.....

Did you make a new LAD for this "simple program"?

If you did, the PLC may not be implementing that LAD if you did not add a JSR to call it.

BCS
 
Last edited:
T4:0 I:1/0 I:1/1 O:4/0
--------[/]--------+-----[ ]------+-----[/]-----------------------------( ) ------|
DN | |
| O:4/0 |
+-----[ ]------+

O:4/0
--------[ ]-------------------------------------------------+-------T:4/0-------+-|
| TON |
| |
| base 1 |
| pre 300|
| acc 0 |
+-------------------+

T4:0 0:4/1
--------[ ]--------------------------------------------------------------( )-----
TT

Cannot toggle or change state in bit table for the input I:1/0
I appreciate all of your help guys. Let me know if I need to furnish anymore information to you regarding the program.
Thanks
 

Similar Topics

So here's my situation, I have been tasked with modifying the logic to mimic a button press in the PLC. I have two identical machines however one...
Replies
6
Views
539
Hello, I'm new to programming. I'm using RSLogix500 to modify an existing program for a SLC500. My plan was to use one of the existing inputs...
Replies
26
Views
1,984
So i have an allen bradley rack (2080-LC50-24QWB), i have it connected through ethernet. I dont have an offline program so im trying to upload...
Replies
6
Views
678
Hi Everyone, I am supporting a system which runs on a SLC 500 (1747-L532). A fault has developed whereby the output state of some digital outputs...
Replies
10
Views
997
Hello, I am currently taking a course on plc programming and in the course rslogix 500 is being used. I am however having a problem since it keeps...
Replies
4
Views
1,701
Back
Top Bottom