Sorry for the question, but after a discussion and betting with an automation colleague, there was a doubt. In the micrologix manual it says:

''MicroLogix 1400 controllers support the following communication protocols
from the primary RS-232/485 communication channel 0 and the RS-232
communication channel 2''


Does this mean that I can connect both RS485 and RS232 devices? Where do I define that channel 0 will be RS232 or RS485? What exactly does that mean? I understand that RS485 or RS232 are pinout configuration and the connector does not matter as long as it has been previously set.
 
You must choose one or the other (RS-232 or RS-485) for the wiring. To choose RS-485, you must pick it in the channel configuration 'RS-485, No Handshaking'
 
Yes. That is the only channel that can support RS-485.

CH2 (the 9-pin D-shaped port) is strictly RS-232, although either channel can support multiple protocols.
 
To be clear: the pinout does matter on Channel 0 for the MicroLogix 1100 and 1400 controllers.

On those controllers, Channel 0 is a single serial port with two different electrical transceivers, for RS-232 and RS-485.

Pins 1, 8, and 2 are connected to the RS485 chip.

Pins 7, 4, and 2 are connected to the the RS-232 chip (Tx, Rx, Gnd) along with Pins 3, 6, and 5 (RTS/CTS and DCD).

To use the RS-485 port for DH485 or Modbus RTU, you configure the port for "485 Network - No Handshaking", which enables the RS-485 transceiver. All the other settings enable the RS-232 transceiver.

The other models of MicroLogix (1000, 1200, and 1500) used Pins 1 and 8 for a +24v DC auxiliary power supply to power up interface modules like the Net-AIC, Net-DNI, and Net-ENI. Such modules are either unpopular or unnecessary in the modern MicroLogix product line.
 

Similar Topics

hello can anyone share with me the diagram of working cable to make the comunication beetwen plc micrologix 1400 and zebra printer trough rs232 or...
Replies
13
Views
6,294
Okay here we go. I am new to this and I need to know the easiest method to mate an Micrologix 1100 to and Automation Direct with RS232. I have a...
Replies
9
Views
2,811
I am having trouble with communication between my micrologix 1000 and my magelis HMIGTO5310 touchscreen i have added the allen bradley df1 driver...
Replies
0
Views
1,483
I am trying to communicate from a Micrologix 1400 chan 2 to a SC2124M scanner via modbus rtu. I have taken a straight through cable with RS232 on...
Replies
8
Views
2,778
Hi:huh::huh::huh: there, I am trying to get an ADAM 4561 converter to talk via RS232 DF1 to a Micrologix 1400. I know that some USB/RS232...
Replies
3
Views
2,675
Back
Top Bottom