silva.foxx
Member
Ever had a failed input on a Siemens PLC?
If, say, I0.0 failed and you had a spare input point, say I1.7, you could strap a link between the two then insert a new network at the TOP of OB1:
'I1.7'..............'I0.0'
|-] [------------( )|
this could temporarily get you out of trouble. If for example you were utilising Input Bytes within your program these would not be affected as they would if you changed all I0.0 to I1.7 manually.
If, say, I0.0 failed and you had a spare input point, say I1.7, you could strap a link between the two then insert a new network at the TOP of OB1:
'I1.7'..............'I0.0'
|-] [------------( )|
this could temporarily get you out of trouble. If for example you were utilising Input Bytes within your program these would not be affected as they would if you changed all I0.0 to I1.7 manually.