I have a PLC5/40 (1785-L40B) series E revision A, with a 1785-ENET series B revision D Ethernet "sidecar" module fitted. Whenever, I cycle power to the PLC, the I.P. address in the 1785-ENET reverts back to 00:00:00:00.

The PLC5 is fitted with an EEPROM and the chassis backplane switch is set to transfer program at powerup. I have checked the offline copy of the PLC program, and all the channel 3A settings are correct.

Anyone got any ideas ?

Thanks in advance, Tim.
 
I don't have a lot of experience with that card but it sounds like the version of the project on your PC may not match the version on the EEPROM.

Sorry if this is too basic, but after you download the project to the PLC-5 did you then transfer it to the EEPROM? I know I will occasionally download to the PLC but forget to transfer to the EEPROM. Then I cycle power and I lose all my changes.

OG
 
Thanks for taking the time to reply.

OG - I thought this might be the problem too, but I've definitely burned the program with the correct Channel 3A settings onto the EEPROM. I've even tried different EEPROMS and another PLC with later revision (E compared to A) firmware.

Gerry - I have got the "BootP" box unchecked in the Channel 3A setup in RSLogix5.

Thanks, Tim.
 
Well the first thing I noticed was the "00:00:00:00" format of the origional post. That is a MAC address format, which should never change.

I hate that BootP is autoenabled on a lot of devices....

Greg
 
Greg Dake said:
Well the first thing I noticed was the "00:00:00:00" format of the origional post. That is a MAC address format, which should never change.

I hate that BootP is autoenabled on a lot of devices....

Greg

by virtue of the colons only; its missing a few more values to be a complete MAC address.
 
I would upgrade Processor and ENET firmware first.
Most likely this is a bug related to this particular combination.
If this did not help try to cycle power without Ethernet cable to see if this is coming from the network.
 
If you have a BootP utility, see if the ENET card is sending out a request for an IP address when you power it up. I'd be curious to see if that is the case.

OG
 
Thanks for the help.

Rockwell Tech Support have advised me to get the firmware updated in both modules, so I'm going down that track.

I tried booting up without the network cable connected, and it didn't make any difference.

I haven't had time to try the BootP utility.

I'll post back when the firmware has been updated.

Thanks again, Tim.
 

Similar Topics

We have many sites with PLC-5s and 1785-ENET sidecars that are being pounded pretty hard by the GE IGS driver (Kepware) and iFIX/Historian...
Replies
1
Views
980
I have a plc 5 with a 1785 ENET card. I'm getting a flashing red stat light. Reading the manual I see its a dual port system call failed. How...
Replies
1
Views
1,844
Hello all. I'm currently trying to configure a 1785-ENET/B module. It is attached to a PLC5/30. When trying to configure it from within rslogix, I...
Replies
2
Views
2,009
I have a PLC5/30 with a 1785-ENET sidecar. Occasionally if I turn power off to the rack for more than a few seconds, the ENET sidecar forgets its...
Replies
0
Views
1,627
I've just changed the IP address for PLC 5/40 with 1785 ENET but I found somethin wrong on RSLinx classic. Last IP is 172.26.52.1 and the new IP...
Replies
8
Views
9,012
Back
Top Bottom