1785-ENET/B Problem
maynarddon
Nov 2006
usa
Hello all. I'm currently trying to configure a 1785-ENET/B module. It is attached to a PLC5/30. When trying to configure it from within rslogix, I get a "Invalid Host Name entered" error.
I've tried both downloading the program with channel 3A already configured and configuring it after I downloaded it. Both with the same results.
I've also tried to bootp it. It does accept the address but I am not able to turn off bootp.
Here's the series and rev info on everything:
Rslogix5 pro v7.20
PLC5/30 Ser A Rev R
1785 Enet/B Ser B Rev D
Thanks for taking the time to read this.
That error message is consistent with a corruption inside the RSLogix 5 project file.
There are several RA Knowledgebase documents that mention that error message.
If you had version 7.30 of RSLogix 5 you could change the 1785-ENET to Series C then back to Series B, which would clear the corrupted Host name.
You could try changing the controller type to a PLC-5E, then back. Anything that will reset the Ethernet Channel settings.
There's also a procedure in the Knowledgebase for exporting the project as a *.PC5, performing manual edits to clear the channel configuration, then re-creating the project.
Thanks Ken for your reply. I did search for the error message, just not in the right place!
Does the 1785 ENET series C refer to the Ethernet/c from within the configuration tab?
thanks again!
We have many sites with PLC-5s and 1785-ENET sidecars that are being pounded pretty hard by the GE IGS driver (Kepware) and iFIX/Historian...
986
I have a plc 5 with a 1785 ENET card. I'm getting a flashing red stat light. Reading the manual I see its a dual port system call failed. How...
1,850
I have a PLC5/30 with a 1785-ENET sidecar. Occasionally if I turn power off to the rack for more than a few seconds, the ENET sidecar forgets its...
1,630
I've just changed the IP address for PLC 5/40 with 1785 ENET but I found somethin wrong on RSLinx classic. Last IP is 172.26.52.1 and the new IP...
9,016
we are having issues with communications with one of our machines. we have 4 machines, and only one of them is losing communications. w are not...
2,097