OkiePC
Lifetime Supporting Member
I have a rack of flex I/O that had a bad module cauising an intermittent local fault on the 1794-ASB module. The rack is used for the main control panel I/O for the machine. The machine was in auto when the fault became persistent, and the operator was unable to stop the machine as it ran out of stock and made a small mess. The E-stop is hardwaired and was finally hit to shut it down.
The flex i/o module 1794-IB16 which caused the fault has been replaced, but before I did that, I inserted contacts in the PLC code to shut down the machine in the case of a RIO fault on that rack.
Well, when there is a local fault on the ASB, the rack fault bit remains cleared, so, as far as I can tell, the PLC cannot detect when this occurs.
Thanks
Paul C.
Does anyone have a workaround for this? I don't like the idea of losing communication with any I/O and not being able to program an orderly shutdown.
The flex i/o module 1794-IB16 which caused the fault has been replaced, but before I did that, I inserted contacts in the PLC code to shut down the machine in the case of a RIO fault on that rack.
Well, when there is a local fault on the ASB, the rack fault bit remains cleared, so, as far as I can tell, the PLC cannot detect when this occurs.
Thanks
Paul C.
Does anyone have a workaround for this? I don't like the idea of losing communication with any I/O and not being able to program an orderly shutdown.