multiple 1794-asb with 1756-dhrio question

lunknowl

Member
Join Date
Oct 2012
Location
vietnam
Posts
37
hi i try to setup 6 1794-asb to a 1756-dhrio channel B. do anyone know how to adjust the dipswitch of the 1794-asb module ?. i already look at the manual but it doesnt mention about 1756-dhrio. thanks
 
Last edited:
do you read my question because answer it? stop provide stupid manual i already read it and nothing mention about 1756-dhrio.i can use the 1747-sn but it only have 0-3 number of rack!anyway it you dont know it stop support
 
Last edited:
I think that you confusion is that the table on Page 2-11 of the 1794-ASB user manual does not list the 1756-DHRIO as a scanner.

It shows the 1747-SN, the PLC-5, the PLC-5/250 and the PLC-3.

That does not mean the 1756-DHRIO and 1794-ASB are incompatible. The DHRIO simply isn't listed in that old manual.

The 1756-DHRIO has two channels that can be configured either for DH+ networking or as RIO Scanners.

Each channel configured as a RIO scanner can support up to 32 physical devices, with up to 32 "logical rack" numbers.

The Rack Numbers are in Octal addressing, and the 1756-DHRIO supports the full range of 00 through 77 (like the PLC-3 did).

If you have six 1794-ASB modules, the simplest thing to do is set them up as "rack" numbers 00, 01, 02, 03, 04, 05.
 
thanks for support, the 1756-dhrio support full range but for the 1794-asb manual the rack dipswitch doest not list 1756-dhrio like you mention so i have the question of dipswitch of 1794-asb ( i dont know if i can setup as same as PLC-5 BECAUSE THE 1747-sn setup only support for 3 rack)
 
I think a apology is called for lunknowl. You were pretty rude to a member that helps many here and gave you the correct info.
 
( i dont know if i can setup as same as PLC-5 BECAUSE THE 1747-sn setup only support for 3 rack)

Yes, you can consider the 1756-DHRIO to be similar to a PLC-5 or PLC-3 controller. It does not have the 4-rack limitation of the 1747-SN.

The RIO protocol was introduced in 1978, so there are a very large set of Allen-Bradley products that use it. Their documentation literally spans decades of time, and may not be perfectly updated and consistent.
 

Similar Topics

This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
Replies
3
Views
147
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
Replies
10
Views
500
I have 9 field devices, three METSEPM5110 power meters and six ACE949-2 rs285 interface modules. I want to read this Modbus rtu data through rs485...
Replies
8
Views
317
I'm trying to use DTM browser to make make modbus poll from RTAC. I'm able to get the points in first poll object. But not able to get anything in...
Replies
1
Views
127
Hello, I encountered a problem with the kinetix 6500 drive, error code s22, loss of 3 phase voltage. After disassembling and replacing the thermal...
Replies
2
Views
170
Back
Top Bottom