We have a request to be able to let the Micromaster drive continue to run after the profibus link is lost.

Is this possible and if so does anyone know what parameters are needed to change on the drive.

Thanks - Joe
 
Sorry, not familiar with Profibus, but once the signal is lost, how will it be controlled? I would assume that it has a separate E-Stop circuit, but no way to control except running to the front of the drive. I wouldn't think it would be a good way to go.

George
 
Don't have manual in front of me...

Obviously there are some HUGE safety concerns, but I think it was parameter P2040 = 0. I will double check parameter number, but it is a watchdog time for telegram failure and if it is zero it no longer timesout if it doesn't receive a setpoint... something like that. Probably shouldn't post without the manual in front of me =)
 
Once Profibus has been lost, what will control the drive ?

I am more familiar with MasterDrives and to prevent a fault when the telegram is lost the telegram failure fault will have to be disabled - I am guessing there is a similar facility in the MicroMaster.
 
rprs258 said:
We have a request to be able to let the Micromaster drive continue to run after the profibus link is lost.
Hi
What do you mean by "Profibus-link lost" (Profibus-cable disconnected or CW1 bit-10 false)?
* At the MM-has a feature -> if drive is set "Running", set CW-1 bit-10 from true to false, take off the profibus-cable -> drive stays running! Don't ask why?? So, If bit-10 is allways true and you disconnect the Profibus-cable the drive stops and gives You an alarm F0070.

Pete 🍻
 

Similar Topics

Folks, We have an older system that was migrated from an SLC to a ControlLogix processor. With this upgrade we also switch, not surprisingly...
Replies
0
Views
2,051
I have a S7-400 with IM153 PA Master connected with the PLC. The IM153 have several couplers to connect with the Profibus PA devices, acting as a...
Replies
3
Views
6,696
Hello, I have a system based on S400 Siemens PLC. On PROFIBUS network are 16 devices, Omron, ABB invertors and SIWAREX modules. We tried to add...
Replies
16
Views
6,660
I am trying to write some code using the AB CLX platform. I have set up a small Profibus network with 3 devices attached. My SST-PFB-CLX Scanner...
Replies
2
Views
4,107
Hi, I was noticing that Profibus connectors have 2 ports on them that can house 2 separate cables. Can I use 2 cables with Profibus signals...
Replies
4
Views
176
Back
Top Bottom