Can anyone help with the folowing? - we want to drive a Danfoss hydraulic valve (PVG 32) with a analogue output signal from a PLC (MITSI or Siemens). The valve requires a proportional signal of 6V to 18V with 12V being the neutral position. (12 to 6V being one direction; 12 to 18V being the other). Can this be done from a standard module?

Thanks in anticipation.
 
The amplifier for driving the valve also applies a dither (an overlayed PWM signal) to the voltage to the valve coil to overcome the effects of static friction on the valve spool. Also the current draw is typically higher than what a PLC will deliver.
 
Hello,


The PVG32 is a proportional valve made for mobile applications. It works with 25-75% of the supply voltage. In mobile applications the only thing that you can be sure about is that you do not have 24V. It can vary depending on battery condition, engine start etc. This way it is possible to make easy joystick control etc. Sauer Danfoss has their own PLC(Plus1) that can interface these valves directly.

However this makes life more difficult when usinga a traditional PLC with 0-10V signal. It is not as easy a getting an amplifier that takes 0-10, or -10/0/+10.

We been doing some tricks with 12V variants of the PVG. This requires 3-9V. Just make sure that the supply voltage is accurate to 12.00V.

You do not need a PWM signal for this valve and the control voltage only require
 
We have been using the PVG 32 proportional valves with electrical actuators for about 5 years in a petrochem environment. They have worked very well for us. Note that this is not a mobile application, so we don't have the problems some people have mentioned with unregulated battery power -- the regulated 24VDC power supply does just fine.

Here's how we control it:

The PLC's digital output module directly drives the actuator's POWER input (pin 1). Energized when operating the valve, de-energized when valve is to be at neutral position.

The PLC's 4-20mA output module feeds a signal conditioner. The signal conditioner output (0-24VDC) is wired to the actuator's CONTROL input (pin 2). Lately we have used the AGM Electronics 4-20mA in/0-24VDC out module, AUX 4000-22. Here's how the signals worked out:
   
SIGNAL
PLC COND. VALVE
OUT OUT POSITION
8mA = 6V = -100%
12mA = 12V = 0%
16mA = 18v = +100%


It's been working reliably ever since it was installed.
 
Last edited:

Similar Topics

Hi I have an electro hydraulic valve with coil resistance 22 ohms that takes as +/-12V DC input with 40Hz dither superimposed. The valve controls...
Replies
7
Views
2,523
I need to control a hydraulic prortional Valve 200-500mA with a S7-1200 PWM output How to set Up? What cycle?
Replies
0
Views
1,701
Has anyone on hear ever heard of controlling a proportional hydraulic valve directly from a PLC with a PWM output and SSR, instead of using an...
Replies
19
Views
5,344
We have a proportional valve where we suspect that we may be at the performance limit. With the performance limit, I mean what I see in a curve of...
Replies
2
Views
2,208
Hello! I have a signal converter, reference PEM - 020 - G24 , which converts a signal of 0-10 V to a current signal that goes to a proportional...
Replies
1
Views
1,878
Back
Top Bottom