Omron C200H Communications Board

keithkyll

Member
Join Date
Jul 2005
Location
Heath, TX
Posts
2,033
I'm servicing a Omron C200HE-CPU42 with C200HW-COMO5-V1. The COMO5 is a dual RS232 module. The customer reports this module won't communicate. I am using CX Programmer V1.2 to monitor.

Voltages appear present on ports. I don't see any errors in SR memory. I have another known good PLC to compare with.

The easy thing to do is replace the module. I'm concerned I may need software to configure the new module. The Communications manual mentions Protocol Support Software. Do I need this to replace a COMO5 Module?
Two PMCR instructions are used in the program.
289.08 (port 1) executes PMCR(87), #1051 (set Alarm), #10, DM4300.
289.12 (PORT 2) executes PMCR(87), #2052 (set PID), #10, DM4400.

This is my first experience with Omron. The PLC is for a Temperature Control Unit.
 
I am no expert, but
I am using CX Programmer V1.2 to monitor
this is a very old version, current version I have is 6.11.

You will need the protocol software, to download the protocol settings for the PMCR instructions.

If you haven't already, I would eliminate the basics first, cable, device's that are communicating with the CPU, addressing, the code that executes the PMCR instructions.

If you get stuck, maybe post a copy of the PMCR instructions for us to look at. gtsupport & jayanthony as well as bobb are pretty conversant with the Omron range.
 
The new software is CX-One. It's a complete suite. I'm using a 30 day trial.
I looked at the data in the existing COM05 card. It has a custom protocol, so I'll need to copy it to the new card. The text shows some 'garbage' characters such as "1/4, 1/2". I suspect the original was programmed with the Japanese version of software. Will I run into problems trying to copy the orginal data from the old card to the new one?
 

Similar Topics

I have a Omron C200H CPU31 PLC and with a C200H-LK201 Host Link Unit plugged into it. I am using CX Programmer and want to be able to communicate...
Replies
5
Views
5,138
I have a sysmac omron plc C200H CPU01,only the power led is ON,using CX-ONE programmer software, and connecting to the plc via Host link LK202-V1...
Replies
2
Views
734
In order to upgrade a control unit, we need to backup program of an omron C200H CPU01 with host link LK202-V1 that has RS422 D9 Connector. Please...
Replies
2
Views
634
The logic seemed to convert nicely, and I had to make changes to the addresses for my AD and DA and 32-point input cards. The current problem is...
Replies
2
Views
1,047
I am trying to display some scaled analog input values on a C-more Micro terminal, from an older C200H Omron PLC. The addresses appear to simply...
Replies
5
Views
2,191