Omron C200H to C-more
bluenoser337
Apr 2003
Nova Scotia
391
I am trying to display some scaled analog input values on a C-more Micro terminal, from an older C200H Omron PLC. The addresses appear to simply be 101, 102, etc. Can I read these addresses directly, and what data type do I specify in the tag and in the display? BCD or unsigned or ?? Going back to try again tomorrow. Thanks!! o_O
Adresses 101, 102 would be IO channels in a C200H.
Do you know what module the values are coming from?
You need to check the module manual to know the format of the number.
gtsuport
Once you get the value scaled as you like it, it will probably be easiest to move that number into a DM register. Then I'm 95% sure the C more can read that address directly.
Thanks for the answers!! Turns out the addressing 101, 102 etc was correct but we were expecting some ambient temperatures to be around 75 degrees and they were coming in at 24 degrees, so I thought the data type must be wrong. Turned out the values were in Celsius. Where's the embarrassed emoticon? :oops: Oh well, a metric screw-up can cause worse problems, I suppose. Search the "Gimli Glider". It's a good story.
Depending on what the module is, there may be a bit you can set to change from degrees C to degrees F.
Gimli Glider, very interesting story. Thanks!
gtsuport
Let me start with I don't have a lot of experience with this so I apologize if this is something dumb. I need to replace an obsolete HMI on one...
1,784
I have a sysmac omron plc C200H CPU01,only the power led is ON,using CX-ONE programmer software, and connecting to the plc via Host link LK202-V1...
708
In order to upgrade a control unit, we need to backup program of an omron C200H CPU01 with host link LK202-V1 that has RS422 D9 Connector. Please...
626
The logic seemed to convert nicely, and I had to make changes to the addresses for my AD and DA and 32-point input cards. The current problem is...
1,037
I have a customer with the Omron C200H that occasionally will start flashing the alarm light and the machine stops. They say they can power down...
3,034