AB program conversion
I am working on converting a AB program over.
Ok, that is all well and good but which processor was the old program for and what are you converting it to?
My question How do I know which outputs are turned on Through a sequential output if my output word is 022.
By the word address you supplied, it looks to be a processor that is pre PLC-5 and uses the old octal addressing. But even if it is not, the answer is still the same. Output word 022 is an output in rack 2 module group 2. Here is where the processor types would be helpful as well as giving information about the I/O system although it is obvious from the word address it is 1771 I/O.
File is 060-063, Mask is 057-057.
This information is telling you where the output information is stored for each of the 4 steps in the sequence. The output bits will be set to the bit pattern of the data stored in these four words. The mask is probably irrelevant in this case if the value being stored is zero in each of the words. However if there is data there,
you have to use that. The mask allows you to transfer data to specific output bits and not others. Everywhere there is a one in the mask word, data is transferred from the source to the destination. Where there is a zero in the word, data is not transferred. So, watch out for the values stored in 057.
My meaning output is a true output on processor outputs modules addresses are 020 021 022.
I have no earthly idea what you are asking here. My English is not to good sometimes either, but I am loath to understand this.
More help is available if better information is forthcoming.