From the description of your problem, the first time you powered the NT600S, there were screens loaded to the unit.
Because you got an SCI Framing Error when trying to download, the Screen Data was corrupted. This is why the NT600S boots to the sytem menu.
1. You must initialize the screen data memory before trying to transmit new screen data.
2. If it continues to fail, this could be due to the new 3.3V technology being used for the new laptop RS232 comm ports. The screen interprets the lower voltage as noise and declares a SCI framing error. This is a known bug with Intel Speedstep technology.
3. This may work. Allow the screen transfer procedure to timeout by removing the connecting cable from the serial port before downloading. After the timeout message reappears, reconnect the cable and download again.
4. If this does not work, take the screen to a desktop computer and try the download procedure ftom a desktop machine.
This bug has been fixed in later screens, but there is no patch for the NT600S becauses it does not use flash memory for the system.
Below find some excerpts from the manual and a link to the Omron download site for this manual.
Precautions to be Observed During the Screen Data Transmission:
When any of the following or a system error occurs during the screen data transmission,
the transmitted screen data will not be registered correctly to the
NT600S. If an error message is displayed in the System Menu and the Transmit
Mode cannot be selected, the screen data memory needs to be initialized.
The power to the NT600S is interrupted or the NT600S is reset.
The power to the computer on which the support tool is running is interrupted or
the computer is reset.
The cable connecting the NT600S to the computer on which the support tool is
running is disconnected or has a broken wire.
The Cancel touch switch on the NT600S screen is pressed to end the transmission
during screen data transfer.
The ESC key on the support tool is pressed to end the transmission.
When the power to the NT600S is turned ON or reset, the screen data is checked.
However, if any of the above occurs during the screen data transmission, the
screen may disappear and other unexpected problems may occur.
In the case of such problems, set DIP SW2-1 to ON to initialize the memory.
http://oeiwcsnts1.omron.com/pdfcata...F00630ADB/$File/M12V022E31299.pdf?OpenElement