I'm having the worst luck with surge protection for field devices. 2 level meters ruined by lightning. I have Phoenix Contact surge protection on 4-20, but it doesn't like it's doing the job. Does anybody other recommendation for other surge protection? I'm possible looking into trying Transtector surge supprestion.
 
If you take a direct hit from lightning all bets are off. I have had good luck with the Phoenix units. Lately I've been using some Allen Bradley blocks (1492-JD3PSSTP) that incorporate a removable fuse and a surge suppression diode connected to ground. Results aren't in yet for long time performance, but they look pretty good. We also use surge suppressor/filters onthe incoming 120 VAC line.

Note that if you don't have a good ground on your panel the surge suppressors won't work.
 
We almost exclusively use Transtector. I usually use the DRDC units for my loops. They are a sacrificial type arrestor, so I have had a few pop. HOWEVER! They have a 5-year UNCONDITIONAL warranty! I haven't yet had a Transtector unit pop that they have not replaced within a week, no questions asked. I also haven't yet, with the exception of one direct hit that basically demolished everything at the site, had a Transtector DRDC or DR120 arrestor let a surge through. Just my $.02
 
Jung,

If you are getting hit often by lightning, then some lightning protection may be needed. As Tom pointed out, for a direct hit there are no surge protectors that will prevent damage.

Lightning protection would not prevent strikes, but it would minimize the damage. There are 3 or 4 types of lightning protection systems. The cheapest, least effective is lightning rods connected to a grounding system. The most effective is overhead wires strung between poles, about 15 feet above the equipment to be protected. The wires are spaced so that a strike within 100 feet cannot reach the equipment (100' strike radius) without first encountering a grounded wire.
 

Similar Topics

I currently have these installed in a few cabinets: https://www.alliedelec.com/phoenix-contact-2920641/70208204/ But they're increasing the mA...
Replies
5
Views
2,456
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
Replies
5
Views
273
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
Replies
7
Views
275
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
Replies
10
Views
1,692
Hi, I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port. When I connected...
Replies
2
Views
486
Back
Top Bottom