SLC5/03<---DH-485--->PC communication setup

Tony2006

Member
Join Date
Oct 2006
Location
Ontario
Posts
4
Hello all,I have a hardware connection below:

SLC 5/03 Channel 0<--->1761-CBL-PM02 cable<--->1761-NET-AIC<--->Belden 9842 cable<--->1761-NET-AIC<--->1761-CBL-PM02 cable<--->PC 9-pin D type RS-232 com1 port.

My question is how to setup RSLinx in PC, also how to configure SLC 5/03 Channel 0 parameters to make DH-485 communication work?

Thanks
 
Last edited:
Open the plc program, click on IO Configuration, then click on CH1 tab. Here the driver block should be set to DH485, the baud to 19200. Make sur ethe node address is set to 1 unless you want a different address. Next go to CH0 tab. The driver should be DF1 full duplex if you have a 9 pin serial port below your DH485 connector on the processor. Kepp the baud at 19200 and stop bits to 1, and no handshaking. This should be the correct setup for you. If not let me know what info you have for these settings.

geoplc
 

Similar Topics

I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
Replies
14
Views
2,555
I am trying to connect to SLC5/03 using an FTDI usb to rs232 with female to female converter at 1 end... however I can not connect to it ... the...
Replies
8
Views
1,270
Good evening. I am in serious need of help. I am trying to connect a Panelview Plus 7 Standard to a SLC5/03(1741-L531) using a Moxa MGate...
Replies
3
Views
636
Hi. I am having trouble establishing comms between an slc5/04 and panel view plus 7 via a PLX51-net-eni. The set up is: 5/04 Channel 0 DF1...
Replies
8
Views
921
Hi All, I have programmed some MSG instruction in SLC5/05 64k CPU series D FW 13 brand new cpu. 2 of the MSG instructions are direct IP to other...
Replies
3
Views
980
Back
Top Bottom