i m facing problem in establishing communication b/w Cimrex 20 and ****


**** is modbus master on RS 485
as per **** it will take updates from slave unit but slave is not connected with any other system how i can update the vlaues from **** to Cimrex 20
and cimrex is modbus slave.
and **** side we have DB 9 connector and on cimrex im using DB25 connector.
but i couldnt succeed

any help will be highly appreciated
regards
 
Most of the time I've set up the HMI as the MODBUS master. It is usually easier that way. Many people think that because the PLC is controlling the process, it has the be the Modbus master. Usually there is a lot more overhead if you make the PLC the modbus master.

As far as cabling, you will have to check the WAGO information for the pin outs on that device. This document will give you the information on the pinouts of the CIMREX

http://hmi.beijerelectronics.com/web/webbfiles.nsf/0/9057BE8496B60148C1256ACD004EA4FC/$File/MA00557F_web.pdf
 
Hello Siby;

From the manual Cimrex terminals installation:


Cimrex20.jpg



This should give you enough details for RS-485 connection on the HMI side; check the corresponding signals on the EWOPN side 9-pin connector and draw a schematic of connections. Buy your D-Sub 9 pin and D-Sub 25 pin connectors, get a hold of adequate cable (2-wire twisted-pair, shielded)for RS-485 transmissions, grab a soldering gun and build the required cable connections.
I noticed that Beijer supports RS-422 communications as a standard, and specifies that for RS-485 there must be some software configurations in the program. Have you taken this into account?
Hope this helps,
Daniel Chartier
 
I have already prepare the cable for ths on cimrex side and **** side i have also selected the option of RS 485 from cimrex software

My **** is not a processor it s connected with WAGO processor
the communication b/w WAGO & **** is on modbus TCP WAGO and **** are communicating and working fine.

here i have one limitation:
MY **** is always master on modbus RS485.
so i cant put Cimrex as modbus master it has to be slave b/c it has the option.

any comment will be highly appreciated
 
Are you getting any communications (maybe garbage or not what you expected) or are you getting nothing?


If you are getting garbage you might need to set the modbus offset and or byte order in the cimrex driver.

If you are getting nothing then there is probably a wiring issue.
 

Similar Topics

in our old machine we used beijer cimrex 41 need to take program backup. i tried it with information designer software through ethernet. ip...
Replies
3
Views
84
Hi. I need to get an upload from a Cimrex 30 HMI. According to a label on the back, it's made by Beijer. See attached photos. It's successfully...
Replies
5
Views
2,599
Hello Everyone, I'm working on a couple of systems that use Beijer HMIs. One system uses a Exter K20m, I connect to it using RS232C serial and I...
Replies
1
Views
2,158
Hi all, We need to change the IP address on an old Beijer Cimrex 91 we have in the field. I know there's a switch that you can change the position...
Replies
0
Views
1,756
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
79
Back
Top Bottom