Allen Bradley communication options..

Cryogen

Member
Join Date
Oct 2005
Location
NH
Posts
151
I have a Micrologix 1200 (24BXB) PLC connected to Panelview std 600. Someone developed this program before me and so far I have been making changes and supporting it. The cable used is 1761-CBL-PM02 together with a null modem. The protocol used on both PLC (CH0) and Panelview is DH485 and I use 1747 PIC/AIC+ driver to view it on RSlinx (we do not have an AIC optical isolator).

Again I am not sure why it is this way but it is. Now, one of our customers want to connect a SLC to this network. What are my options?
 
Last edited:
I glanced through the manual real quick. I am sure I can find the answer but how will the connections be with this module? ML1200 to AIC+ and from there to the SLC and PV?
 
Last edited:
I agree with Ron - the convenience of having an AIC+ for each device outweighs the extra cost.

One caution is the cabling of the PV-600 to the AIC+. The standard A-B cable that connects to the AIC+ DB-9 port includes a power connection, and this can fault the network. Use a cable that only hast RX, TX, and SG in it.
 

Similar Topics

Hi good day Everyone, I have a cimplicity v10 project with 7 to 8k tags communicating with AB PLC through OPC and Rslinx classic. I have this...
Replies
3
Views
218
Hi Everyone, I am currently trying to communicate ControlLogix PLCs via EtherNet/IP with Delta V DCS. There is a VIM2 card configured for...
Replies
1
Views
279
I was trying to communicate between Siemens ET200S IM-151-8 PN/DP CPU to Rockwell Allen Bradley L73 through Hilscher Gateway NT100-RE-EN. Using...
Replies
0
Views
111
Hi All! I have a project where communication needed between an Allen Bradley CLX and a Rexroth CML25. Do anybody have experience with it? We...
Replies
4
Views
781
hello, we are using allen bradley plc 5/15 with uticor hmi pv700. but now we replace plc 5/15 with 5/20 but the uticor hmi is not communicating...
Replies
0
Views
919
Back
Top Bottom