I have been working with a s7 400 plc. I added a couple networks and the on downloads I get a message that there is not anough memory to load.I cant beleave this because I only added a move statement and a m bit. Is there a setting that could be wrong in the maneger that would cause this or any other Ideas?
 
I just feel like the program is not that big and there should not be a problem like this
 
Last edited:
another thing, it downloads the whole block not just the changed networks, so if the block is quite big and you have not much memory left then you will get the memory full message.
 
adamjones said:
I just feel like the program is not that big and there should not be a problem like this

When you go to the compress memory page, it will show you graphically how much memory you have and how much used.
 
It does and it says it full.I Just wanted to make sure that there wasnt some type of setting that I missed. Allof my siemans expirenance has been with win ac with the soft PLCS. I dided know if I missed something
 
Don't forget, the memory used may have built up, when was the PLC last compressed or downloaded?

Small changes over months, maybe years, could have accumulated, so it may not only be your modification.
 

Similar Topics

ml1400 (1766 L32BXB) problems with communicacion ascii I configured the channel 2 like ascii, 9600 baudios, parity none, stop bit 1 , data bit 1...
Replies
1
Views
1,801
Hi guys, Im currently working on a project that involves cycling pieces manufactured at my work. Almost finished but I started having problems...
Replies
3
Views
2,989
Hi all, I was trying to use get block in S7-400 for communicate with S7-1200 CPU. I have a lot of questions: 1) In S7 communications, how can I...
Replies
2
Views
2,218
Hi all, I am adding an endress hauser promag w 400 into a plant wide monitoring system. It is a CompactLogix RS5000 system. It seemed easy to add...
Replies
16
Views
11,339
Hi, I have a new Siemens 400H-CPU. On the rack there is a power module, a CPU and an ethernet card. I need to download the hardware...
Replies
2
Views
1,986
Back
Top Bottom