about Panel view plus 1000

DarkLord81

Member
Join Date
Feb 2007
Location
sonora
Posts
3
Hi, I'm request for help to configure a panel view 1000 plus, and connect it to a micrologix 1500 LRP, I've configure the tags, the communications (DH485), and it doesn't work, it just say that is no communications between PLC and Panel view, if anybody can help me, it will be great. Thanks
 
Describe the cables you are using.

Describe the configuration of the MicroLogix serial port.

Generally I would just use a straight-through serial cable between the RS232 port on the PanelView Plus and the RS232 port on the MicroLogix 1500 (Channel 1) with DF1 Full Duplex protocol.
 
Hi

I'm using a NET AIC to connect the PLC and Panel view 1000 plus, I'm using the port 1 with a 1761-CBL-PM02 conected to the NET AIC, and the panel view conected directly to the NET AIC via DH 485 port. My question is if that is correct o I missing somethig and if I need to configure something special in the PLC or the panel view. Thanks
 
Let me re-iterate so I'm clear on this.

The MicroLogix 1764-LRP Channel 1 (the 9-pin port on the left side) is connected to the 8-pin round plug on the 1761-NET-AIC using a 1761-CBL-PM02 cable.

The PanelView has a 2711-RN6 card whose screw-terminal connector is cabled to the screw-terminal connector on the 1761-NET-AIC module. This cable should just be Data A, Data B, Common, and Shield. Termination jumpers should be in place on both ends.


The first important thing is to be certain that Channel 1 of the MicroLogix is configured for DH485 protocol in RSLogix 500. Make a note of what network address (node number) the MicroLogix 1500 is using for that port.

The second thing is to examine the RSLinx Enterprise configuration to be sure it's configured for DH485, with a unique node address of it's own.

The third thing is to examine the RSLinx Enterprise Shortcut configuration to be sure that it's configured in the Target tab drive and node that points it to the MicroLogix 1500.
 
Hello

Ok, in the first point I´ve have a mistake, because I configure the channel 1 for DF1 Full Duplex in the RSlogix 500, in the second point there is no problem, in the third point I have a question... I guess that the shorcuts are a label to identify each device on the network, because the syntax of the direccions of the tags is:
[Shortcut]Address

Is that correct?? Because I have one shortcut on the device of the NET AIC connected to PLC.

Another question. In the configuration of the MSG instruccion, what should be the right configuration to communicate the PLC with Panel view??

I have: Communication Command : 500 CPU write
Data Table address: N7:0
Size in elements: 8

Target Device
Data Table address: N7:0
Local node address: 2
Local/remote: Local

I'm interested in the communication command and local/remote if i'm right.

I hope that you can help me with this, because I have 1 week with this, thanks
 

Similar Topics

Am asking if we can upgrade sd ram and cf card of panel view plus ab by a normal sd ram and cf card but Allen Bradley to save cost because in ab...
Replies
9
Views
299
Good morning, I have a question, I would like to know if I can send an Excel file to an email from my panel view and see how it is possible to...
Replies
1
Views
170
I want to run a factory talk view ME project in a Panel View Plus 7 Performance HMI. The project was developed in a 'Windows 7 Professional 64 bit...
Replies
5
Views
345
I purchased a used PanelView Plus 1000 to learn get familiar with the software. Seems to be a pretty popular HMI. I can ping the HMI but I cannot...
Replies
6
Views
905
Hello, hope yall are doing well. I have a HMI program where I need to add a "GoToDisplay" button, so when this button is pressed, it goes to a...
Replies
5
Views
907
Back
Top Bottom