Can I wire a 4-20ma input to two different input cards in series or parallel? I have 2 plcs that both have current input cards, 1 card is wired in series to the transmitter; can I tap into the 1st card as is or would I need to add the 2nd cards input in series with the 1st cards input?

Thanks
 
You will need to make sure that at least one card HAS BOTH input terminals floating, not tied to ground. That card will be the first one to connect to.


Another trick (incase neither card has both input terminals floating) is to use/set the 2nd card to voltage input and parallel its input to the first card. This takes advantage of the built in resistor in the first card. BTW, do NOT assume the resistor is 250 ohms. I've seen 25 and 2.5 ohm resistors used.
 
When using a ControlLogix 1756-IF16 we've tried both running them in series and parralleling the voltage. We've seen issues where when the "first" PLC is de-energized we get a 0.1mA loss of current seen by the second. We're attributing this to the fact that the analog input uses active components with high impedance when energized, but when de-energized allows some current to get back to ground.

Besides using a signal splitter (single point of failure) has anyone had any experience with this?
 

Similar Topics

Hi All, Has any of you tried to change the IP Gateway of the PLC (of course, essentially of the ENBT card), while in a redundant configuration...
Replies
3
Views
150
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
4
Views
179
Hi, we are using Rx3i CRU320 redundant PLC system and we noticed a discrepancy between Primary and Secondary controller. Couple of variables (DI)...
Replies
8
Views
325
Hello, I have a pair of redundant 1756-L71 controllers rev 24. These controllers currently have produced and consumed tag interfaces to 3 other...
Replies
2
Views
231
I have a L82 system setup redundant that i need to download a lot of programs to in a critical environment. What is the process to do this and...
Replies
10
Views
341
Back
Top Bottom