Hi,

I've been asked to design a system based on Omron CJ1M PLC. This is my first time doing that kind of job so I'm a bit confused. I have some doubts related to the power supply.

I need to feed the following modules (current consumption between "( )"):

- CJ1M-CPU11-ETN (0.58A, 5V)
- CJ1W-OC211 (0.096A, 24VDC)
- CJ1W-ID211 (0.08A, 5VDC)
- CJ1W-AD041-V1 (input signals (2): 1-10V, 4-20mA)
- CJ1W-DRM21 (0.29A, 5V)

So, as far as I understand I need two power supplies: one for the output relay module and one for the rest of the modules. So two CJ1W-PA202 modules would be right to power the system? Or am I just plain wrong?

Thanks in advance,

Sebastián.
 
Last edited:
This follows standard hardware configuration, not just Omron.

The modules are powered from the PA202, which is part of the backplane.

The OC211 needs a seperate 24VDC supply to power the outputs that are switched by the module
 
You need only one PA202 power supply. The PA202 generates both 5V and 24V internally and can provide upto 0.4A (and the OC211 card needs only 0.096A)

SVN
 
Use the PA202 to power the PLC internals. You really need a separate power supply for the outputs - talk to your Omron distributor.
 
(and the OC211 card needs only 0.096A)

Does this include the output loads?

You really need a separate power supply for the outputs - talk to your Omron distributor.


This is the normal way to go, occasionally, on smaller systems, sometimes the onboard PSU is sufficient, but more than likely a
seperate supply is used.
 
Just for the record:

FuentedePoder.jpg


So just one power supply would be enough.

Thanks you all.
 
If you have a look in the CJ1 Operation Manual Appendix A - specifications of basic I/O units - the connections for relay output card type CJ1W-OC211 at the terminal connections it clearly shows an external power supply needs to be connected to drive the outputs. The reference you made above is to internal card consumption from the rack. How can the current draw for the card be so low on the 24VDC side if your load per relay is 1 amp - x 16 = 16 amps. The rack cannot supply that sort of power.

The CPU power supplies also do NOT have an extrnal connection to supply 24VDC to anything.

You even have to supply an external 24VDC power supply for the input cards as well.

Use an external power supply for your I/O!!!!!
 
Not to gang up, but Bob is right.

Keep it simple.

Unless of course the poster has confused us.

would be right to power the system?

Maybe he was only asking about system configuration, and he/she
plans on using an external supply for his/her IO.
 
Scott, I get the impression that this person is under the impression that the relay outputs are powered from the rack power supply. This is not the case only the relay coils and LED indicators are powered from the rack - the relay contacts have to be powered from an external power supply.
 
scottmurphy said:
Maybe he was only asking about system configuration, and he/she
plans on using an external supply for his/her IO.

From the original post I also thought so, thats why I said only one PA202 is required. He was asking whether two PA202s are required or one.

SVN
 
You cannot use 2 PA202s - only one can fit on the rack. They are designed to power the CPU/rack only - not outside stuff. They are noty a general power supply.Suggest he talks to his Omron distributor about a separate switchmode power supply to supply power for the I/O.
 

Similar Topics

Hi all, I took a PLC class some time ago and have since forgotten almost everything in it. I think I can work out the programming again but I'm...
Replies
4
Views
1,751
I work in a field where our plc and hmi are constantly being powered fully off and on daily before being sent out. I am new to the world of plc...
Replies
5
Views
971
Please laugh… but can I take 24volts from an IO module and wire it straight into its own input card to simulate an input….?
Replies
5
Views
1,279
I need to be able to open a customer's FT View project and make any changes if necessary. Which one do I need??? :hmmm: I don't want to have...
Replies
10
Views
2,601
Hello all, i will start off by saying i know nothing about load cells, i want a converter/amplifier to output a 4/20mA signal from a load cell...
Replies
14
Views
5,420
Back
Top Bottom