If you can get a 1770-KFD or 1784-PCD to go online with the network, you're going to be a lot happier. The 1747-SDNPT and 1771-SDNPT passthrough drivers are better than nothing, but they are dog-slow compared to a direct network interface.
The 1771-SDN is just a big multiple-block-transfer module from the PLC-5's perspective.
You can have several block transfers to the same slot, differentiated only by their size. The control/status word is Word 0 of the block transfer that is 62 Words in length.
I try to not use both channels of the 1771-SDN if I don't have to. It can get confusing managing the scanlist downloads for both channels, though there are some Knowbase articles that explain it.