I'm confused! which is the correct way to connect an analog sensor? top circuit is from the AB1762-IF4 manual lower one from the Redlion manual.

Transmitter2.JPG
 
RYoumans said:
The top one is the preferred way.

Why??

If the transmitters are current TX (i.e 4-20 ma) then they are both correct.
The current is the same in a series circuit.
 
Yes, a loop is a loop. It's just better practice to have power supplies feed the transmitter first, and then the measuring device. This is the way you'll see it wired most of the time.
 
RYoumans said:
Yes, a loop is a loop. It's just better practice to have power supplies feed the transmitter first, and then the measuring device. This is the way you'll see it wired most of the time.

Ok. I too connect it like the top drawing, I like to fuse the "+" connections from the PS to the Transmitter. The TX is usually outside the cabinet and the PS and I/O module are inside. I like to protect against any thing going bad in the outside world.
But better practice? And thats the way you see it most of the time. Not so sure of that.( maybe)
 
From the installation instruction for the 1762-IF4 (Not IF4I)






System Wiring Guidelines​



Consider the following when wiring your system:





• All module commons (ANLG COM) are connected in the analog module.


The analog common (ANLG COM) is not connected to earth ground inside the module.​

• Do not use the analog module’s NC terminals as connection points.​

• Channels are not isolated from each other.​

• Use Belden™ 8761, or equivalent, shielded wire.​

• Under normal conditions, the drain wire and shield junction must be connected to earth ground via a panel or DIN rail mounting screw at the analog I/O module end. Keep the shield connection to ground as short as possible.​
(1)






• To ensure optimum accuracy, limit overall cable impedance by keeping your cable as short as possible. Locate the I/O system as close to your sensors or actuators as your application will permit.​



• If multiple power supplies are used with analog inputs, the power supply commons must be connected.​



Bottom line, I think either way will work for one sensor. I think you will have problems wiring more than one sensor with the bottom arrangement.
 
Last edited:

Similar Topics

Hi, We have a bag in box machine with a few payoffs that unroll foil. The inverters are PowerFlex 525 and the tension rollers mechanism is...
Replies
4
Views
802
Hi, I have a bit of PLC experience in Siemens and have unfortunately been blessed with working on Automation Studio and B&R which has been a big...
Replies
5
Views
1,364
Hi, I am working on a project with Delta PLC for the first time. I want to connect a Sinking analog sensor (4-20 mA) to a Delta analog module...
Replies
0
Views
1,662
Curious, is it common to program in offsets to calibrate/correct analog sensor readings in certain applications? As an example, I have a couple...
Replies
11
Views
3,114
I have a Bentley Nevada Velocity sensor that claims to spit out a 100 mv/IPS signal. I'm being told that it will work with an analog input card...
Replies
11
Views
7,025
Back
Top Bottom