Dear Everyone,

Today I have faced a problem regarding channel 0 of the 331-7KB02-0AB0 AI 2X12 bit module. I have attached the wiring diagram.

331_7KB02_0AB0.JPG


step 1. I have used digital meter to measure 4-20mA current by removing wire at terminal no.2 (of module) by keeping the meter in series with terminal no.2 ----- Found No current.

331_7KB02_0AB0currentzero.JPG


step 2. I removed wire at terminal no.2 (kept it open) and connected the meter in series with terminal no.3 (of module).....I have found current in accordance with pressure.

331_7KB02_0AB0_current_not_zero.JPG


Does it mean that channel0 is faulty?

There are no other faulty indications as well as hardware diagnostics is also ok.

Thanks in advance.
 
Maybe you already have it.

http://mediaibox.siemens.com.br/upfiles/1123.pdf

on page 238 en 239 the wiring is shown, and the possible configuration of the input.
I do not have the hardwaremanual here but there is black configuration block on the left side marked with a-b-c-d as shown on page 239.

For mA the signal must connected to terminal 2+ and 3- for channel 0. The only limatation is the diif voltage between 3- en 20- is 2,5 Volt. And not for two wire transmitters
 
Last edited:

Similar Topics

Hello dears any body can tell me about6ES7 331-1KF01-0AB0 i have to connect pt 100 with std range my wiring connection or ok cpu says card...
Replies
2
Views
3,561
Hey when I turn on my Siemens PLC CPU 216-2 after runing 10 minute it's stop and showing SF indication after I turn off and some time later turn...
Replies
0
Views
162
Good Morning , Not sure how many use Markem-Imaje SmartDate X60 Printers , but I'm having trouble finding a good manual for...
Replies
5
Views
745
I'll preface this by saying this is the first time I've worked on a Siemens system and I'm fairly unfamiliar with them. I might mess up some of...
Replies
29
Views
867
Hello all, First time poster, long time viewer of these forums. Could not find my solution on here. We have had issues with a Comm Fail on an...
Replies
2
Views
437
Back
Top Bottom