RSNetworx For Dnet Tag Generator

plcengineer

Member
Join Date
Jan 2004
Location
USA
Posts
176
I ran this utility today and it appeared to work ok. However, when I went to pull in an E-3 relay, I only seen three bits in the output word, OutA, OutB and Trip Reset. Where do I stroke the bit for pulling in the E-3. Also, I energized the Trip Reset bit and it didn't reset a fault..

Pleaese Advise
 
Generally Output A = Run Forward, but it's entirely up to how you have the overload wired to the contactor.

Make sure you have the scanlist downloaded to the 1756-DNB (the Tag Generator Utility doesn't do this for you) and that the 1756-DNB is successfully in RUN mode by setting the RUN bit in the command word.
 