danesh Member D Join Date Jul 2005 Location Teh Posts 88 Mar 9, 2008 #1 Dear friends, I want to communicate a DCS system that runs at S7-414-4H to a ESD system that runs at Hima plc, are you have any experience in this case? With which protocol they can interconnect? Regards, Danesh
Dear friends, I want to communicate a DCS system that runs at S7-414-4H to a ESD system that runs at Hima plc, are you have any experience in this case? With which protocol they can interconnect? Regards, Danesh
dchartier Member D Join Date May 2003 Posts 1,546 Mar 9, 2008 #2 Hello danesh; A few minutes on the HIMA site showed this link to the HIMA comm modules: http://www.hima.com/Products/Planar4/Communication_modules.php Yopu could look into Profibus-DP, Modbus or OPC. Hope this helps, Daniel Chartier
Hello danesh; A few minutes on the HIMA site showed this link to the HIMA comm modules: http://www.hima.com/Products/Planar4/Communication_modules.php Yopu could look into Profibus-DP, Modbus or OPC. Hope this helps, Daniel Chartier