I am new to using Wago I/O. For this project I am using a number of 750-833 Programmable Fieldbus controllers.

On each controller there is 14 Analog Inputs and 4 DI's and 2 DO's. My questions are as follows:

1. Does it matter which way I arrange the Modular I/O? i.e Analogs before digitals?

2. I need to perform some scaling in the 750-833 controller for each analog input (14).This will be read by the Profibus Master (Prosoft MV156-PDPM on a CLX Rack) Is it possible to write a function to do this in 750-833 and call it 14 times? Are these controllers capable of this? Project requires some desision making remotely in event of a fieldbus or PLC failure.
 
1. Does it matter which way I arrange the Modular I/O? i.e Analogs before digitals?

Wago as a funny way of having the i/o modules address in a particular order. IF you plan on adding ANY other analog or Word consumming module in the futur... find out about how to OFFSET the i/o adresses. If not then just let it be like you want.

The analog and Word consumming module will take the first addreses by default and what comes next will be the digital modules.. from left to right...(ENJOYE):)

2. I need to perform some scaling in the 750-833 controller for each analog input (14).This will be read by the Profibus Master (Prosoft MV156-PDPM on a CLX Rack) Is it possible to write a function to do this in 750-833 and call it 14 times? Are these controllers capable of this? Project requires some desision making remotely in event of a fieldbus or PLC failure.

Ther PFC is just like a PLC with a particular com device attached. So you can write a full program into it. Of course maths are enabled... yoou can also write some routine ladder that will act IF the feildbus con. is lost.
 
no problem even mixing is possible although not advisable.
first use the analog channels from left to right on the module.
They will take up the words like %IW0 till %IW14
yes scaling is no problem or use linear2 for a straight line or use linear10 for example when line curved.
yes calling several times no problem.
wago is my specialty.
[email protected]
 

Similar Topics

Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
79
I have a project to setup base programs across multiple PLC platforms that can be used for Modbus communications to various sensors that have...
Replies
0
Views
121
Hello, I m having a problem with wago 750-862 plc. The plc won't start automatically in run mode after a power reboot. I've also tried the...
Replies
4
Views
355
Hello everyone, I am trying to setup a Wago 750-8100 PLC to send a text message out via ethernet port, if I get a Digital input that is true. I...
Replies
0
Views
344
How do you set up a message block for a REMOTE IO unit? (using ethernet IP)?
Replies
1
Views
594
Back
Top Bottom