Reviewing customer provided SLC layout and has an abundance of RIO devices...So many in fact that I want to understand clearly any limitiations or gotchas I should be aware of when setting up BTR/BTWs.....
Layout:
Main SLC 505 base with 10 slot Rack and 10 slot extender
Three SN modules in Slots 1,2,3
Slot 1:
R0G0 7 Slot Rack - 2 slot addr (alternating I/O) - 1/2 rack
remaining RGs - (10) 1/4 rack weigh controllers
Slot2:
R0G3 7 Slot Rack - 2 slot addr (alternating I/O) - 1/2 rack
remaining RGs - (8) 1/4 rack PF70s
Slot3:
remaining RGs - (12) 1/4 rack PF70s
The 7 Slot Racks are discrete only, so no BTR/BTWs there. So, I have 30 devices that need BTR/BTW. I know the SLC has a max Block Xfer buffer of 32, but what I'm not clear on is that 32 BTRs and 32BTWs or is that 32 total? If 32 total, how do I ensure that I don't overrun the buffer. I've normally done bi-dirctional BTR/BTW combos and would like to continue to do so. But do I need to add additional control bits in the enable rung from the other BTR/BTWs to prohibit them from all firing at once?
Thanks!
Layout:
Main SLC 505 base with 10 slot Rack and 10 slot extender
Three SN modules in Slots 1,2,3
Slot 1:
R0G0 7 Slot Rack - 2 slot addr (alternating I/O) - 1/2 rack
remaining RGs - (10) 1/4 rack weigh controllers
Slot2:
R0G3 7 Slot Rack - 2 slot addr (alternating I/O) - 1/2 rack
remaining RGs - (8) 1/4 rack PF70s
Slot3:
remaining RGs - (12) 1/4 rack PF70s
The 7 Slot Racks are discrete only, so no BTR/BTWs there. So, I have 30 devices that need BTR/BTW. I know the SLC has a max Block Xfer buffer of 32, but what I'm not clear on is that 32 BTRs and 32BTWs or is that 32 total? If 32 total, how do I ensure that I don't overrun the buffer. I've normally done bi-dirctional BTR/BTW combos and would like to continue to do so. But do I need to add additional control bits in the enable rung from the other BTR/BTWs to prohibit them from all firing at once?
Thanks!