wilsonzhu Member W Join Date Jan 2008 Location vancouver Posts 278 Apr 2, 2008 #1 How to set the tempeture scale of plc5's 1771-ixe Themocouple input in Rslogix 5?
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Apr 2, 2008 #2 You don't set the scale. You just configure the card for the type of thermocouple that is connected to it and the raw data will be in degrees "F" or "C" directly. see sample config below also links for the manuals http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1771-in049_-en-p.pdf http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1771-um658_-en-p.pdf
You don't set the scale. You just configure the card for the type of thermocouple that is connected to it and the raw data will be in degrees "F" or "C" directly. see sample config below also links for the manuals http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1771-in049_-en-p.pdf http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1771-um658_-en-p.pdf
wilsonzhu Member OP W Join Date Jan 2008 Location vancouver Posts 278 Apr 3, 2008 #3 Thanks, Can you please check my another post about N file in PLC5. I really appreciate it.